    Setting of earth fault relay

    A 20 KV switchgear have equipped with one zig-zag earthing transformer. As you know,
    A grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults. If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 100 KVA.
    The primary current setting of related earth fault relay that installed in neutral point of E.T. is 8 Amp.
    This set point current is chosen in base of E.T. continuous rating current and following calculations:

    It =100/ (20x1.73) = 2.89 A

    In= 3x It = 8.67 A

    But the earth fault current calculation and analyses dictate other primary current setting (12.5 A).

    Which one current setting is correct? Which one do you choose?



    --------------------------------------
    Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
  2. #2
    2007/10/18
    27
    1

    پاسخ : Setting of earth fault relay

    Unfortunately, nowadays with our world information transmission system (internet), we usually neglect the basic conceptions and deep thinking about new problems.
    With more deep thinking, we can find that the mentioned evident equation (S = 1.73 VI) is not correct for zig-zag earthing transformers.
    Indeed, each leg of a grounding transformer carries one-third of the neutral current and has line-to-neutral voltage. So in a grounded wye - delta transformer, the total power rating including all three phases is the neutral current times
    The line-to-ground voltage:
    S= 1.73 VI
    But a zig-zag transformer is more efficient than a grounded wye - delta transformer.
    In a zig-zag, each winding has less than the line-to-ground voltage,
    by a factor of 1.73, so the bank may be rated lower:
    S = 1.73/1.7.3 VI = VI
    Therefore, the continuous rating current of E/T is 5 A and rating neutral current is 15A, and we can choose 12.5A as correct earth fault primary current setting.


    --------------------------------------
    Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
نمایش نتایج: از 1 به 2 از 2

موضوعات مشابه

  1. SHT11 & LCD 16*2 & RELAY +SURSE COD + PCB
    توسط mohsen.hex در انجمن پروژه ها و مقالات تكميل شده AVR
    پاسخ: 4
    آخرين نوشته: 2015/11/10, 22:58
  2. پاسخ: 7
    آخرين نوشته: 2013/10/20, 23:51
  3. ** نقشه های google earth ، ارتباط GPS با google earth , tracking ...
    توسط masoud9 در انجمن كامپيوتر ، اينترنت و علوم مرتبط
    پاسخ: 17
    آخرين نوشته: 2012/05/06, 22:22
  4. shunt relay trip
    توسط مرتضي ك در انجمن سيستم هاي قدرت
    پاسخ: 2
    آخرين نوشته: 2009/10/18, 18:36
  5. انواع fault
    توسط hossein.farahmandfar در انجمن حفاظت سیستمهای قدرت
    پاسخ: 1
    آخرين نوشته: 2009/08/23, 02:50

کلمات کلیدی این موضوع

علاقه مندي ها (Bookmarks)

علاقه مندي ها (Bookmarks)

مجوز های ارسال و ویرایش

  • شما نمیتوانید موضوع جدیدی ارسال کنید
  • شما امکان ارسال پاسخ را ندارید
  • شما نمیتوانید فایل پیوست کنید.
  • شما نمیتوانید پست های خود را ویرایش کنید
  •